Calculating maximum values of earth fault loop impedance from device characteristics.
► Support this channel:
Patreon: / jwflame
PayPal Donations: xo4.uk/?PPP
► Social Media:
Twitter: / jwflame
Facebook: / jwflame
Instagram: / jwflame
► Contact info, sending stuff in: etc.:
xo4.uk/?YTT
► Website - More on this video and many other subjects
Website: flameport.com

Пікірлер
  • John, I'd honestly pay a subscription price to view your video's. Outstanding quality and excellent presentation to fully cover all areas.

    @MK-wf1eg@MK-wf1eg2 жыл бұрын
  • Who are giving Mr Ward a thumbs down? Why ? Free, clear, accurate advice for anyone in the Industry or not, how can that be criticised ?

    @rossmurdoch1886@rossmurdoch18862 жыл бұрын
    • People that spend all of their lives clicking the thumbs down do exist. You can even pay dubious types to make a certain number of thumbs down, or other things. In the end, it makes no difference to anyone or anything.

      @jwflame@jwflame2 жыл бұрын
    • @@jwflame it just grinds my gears when guys like you give your time to help the less informed get better equipped to keep safe and learn what this industry is all about. You clearly rise above such nonsense as I expected Thanks for all your content John it really is first class

      @rossmurdoch7870@rossmurdoch78702 жыл бұрын
  • I've been trying to understand this for weeks now. Once again you have explained it so clearly, I've have finally fully grasped it. Thank you from a mature learner 👍

    @adeytecnic@adeytecnic3 жыл бұрын
  • This maths I learnt in College in 1990 as part of my Electrical training course Love your videos nice to see someone on KZhead who really knows their stuff

    @markfire1235@markfire12353 жыл бұрын
  • The 80% rule of thumb is given by the simplified temperature coefficient for copper conductors 0.004, for a 70deg conductor measured at 10deg the change is 60 degrees. (60x0.004)+1 gives a factor of 1.24, the reciprocal of this being 0.8 ish (or 80%). It used to be explained quite well in the 16th edn of GN3 in the appendix, I don't think it is as clear in the newer versions.

    @cumberland1234@cumberland12343 жыл бұрын
  • John, thanks for all the clear video's. As a starter, they really make me understand things much better. I even get enthousiastic about the topics!

    @rickcrompvoets6799@rickcrompvoets67993 жыл бұрын
  • Excellent video John, You make learning so much easier, I'd forgotten all about it as I have been out of the game for about ten years, so I am now teaching myself to get me up to date with the regs and so on. Thank you keep up the good work.

    @seandempsey9396@seandempsey93963 жыл бұрын
  • This is so well explained. Any apprentice should be watching these especially if they have a bad teacher or they will fail exams when it could be avoided. Thank you

    @michaelcostello6991@michaelcostello69912 жыл бұрын
  • I have tried for so long to find out what this mock question is asking me and all I could find was 20 minute videos talking in circles about irrelevant crap and your video has cleared up the problem in 4 mins. I'm so happy to get over this stupid question!

    @Anarcaeful@Anarcaeful Жыл бұрын
  • John Ward, This awesome calculation and really useful as new electrician which really very much appreciate your time Thanks again

    @mohamedsiadabdille7631@mohamedsiadabdille7631 Жыл бұрын
  • John I once took the piss for your painted radiators, even though your videos always pull me out of potential shit. So to show my gratitude I'm going to paint mine the same colour in honour of you. To the dismay of my mrs. Thanks for the clear videos

    @Seanmcleod84@Seanmcleod843 жыл бұрын
  • Thanks JW, for another great video of Zs Impedance 👍🏿

    @triplerjm2353@triplerjm23533 жыл бұрын
  • Clearly explained as always John

    @rossmurdoch1886@rossmurdoch18863 жыл бұрын
  • Cheers, Thank you for taking the the time to explain 👍

    @teyronjayneevans3278@teyronjayneevans32783 жыл бұрын
  • Thank you John, another clear and precise explanation on all things electrical. 🍻

    @Steve-ho4pq@Steve-ho4pq3 жыл бұрын
  • Great vid as always JW! Thank you for helping me through my 2365 with your videos!

    @jameshansing5396@jameshansing53963 жыл бұрын
  • Thanks John, as always

    @TargaEcommerce@TargaEcommerce3 жыл бұрын
  • John! Very well explained! Love your videos!👍

    @malachygallagher4936@malachygallagher49363 жыл бұрын
  • Made it easy for me john great video as I'm doing my 18th regs keep it coming 👍

    @Egypt1962@Egypt19623 жыл бұрын
  • Brilliantly explained!

    @brewertonpaul@brewertonpaul3 жыл бұрын
  • Thanks JW...as always " good job "

    @stevencretney9495@stevencretney94953 жыл бұрын
  • Thanks for your great explinations, and for you work to make this video!

    @descultualexandru4022@descultualexandru40222 жыл бұрын
  • Absolutely excellent video John is the maestro

    @steveokinevo@steveokinevo3 жыл бұрын
  • thanks John it makes more sence with your step by step ..

    @markadamson3801@markadamson38012 жыл бұрын
  • Excellent explanation. Thank you

    @stephenwatkins3175@stephenwatkins31753 жыл бұрын
  • Very good enjoyed listening

    @alunroberts1439@alunroberts14397 ай бұрын
  • Thank you Mr Ward , once again 👍

    @williammartinculleton7523@williammartinculleton75233 жыл бұрын
  • Great knowledge video. Thank you for sharing

    @Keith12001@Keith120013 жыл бұрын
  • Thanks. I'm a Quality Cx Administrator for an engineering/construction company and this equation will be used in an excel formula for Zs ratings.

    @nssdesigns@nssdesigns3 жыл бұрын
  • Another awesome video 😺✨💋 Thanks JW

    @jhc_fan@jhc_fan3 жыл бұрын
  • One word. CLASS!!!

    @keithlatty@keithlatty3 жыл бұрын
  • Great video, very well explained, thank you

    @craigdiver@craigdiver3 жыл бұрын
  • I thought you look up the time/ current characteristics of the device and read off at the disconnect time required ( o.4, 1, 5 s etc) on the graph and use that current value to calculate?

    @danielstimpson7792@danielstimpson77927 ай бұрын
  • Who thumbs down jp someone had they arse handed to them and can't take criticism, trust in jp our electrical god

    @ianhill20101@ianhill201013 жыл бұрын
  • Hi John, thanks for the great videos - well helpful. Does the 'rule of thumb' apply to all values in BS671:2018 such as cable current carrying capacities ?

    @AirBournePixels@AirBournePixels2 жыл бұрын
  • Superb piece of work Thankyou.

    @DMFPERFORMANCE@DMFPERFORMANCE3 жыл бұрын
  • Great explanation.

    @SqwarkParrotSpittingFeathers@SqwarkParrotSpittingFeathers3 жыл бұрын
  • Nice video John keep them coming your a star

    @stephencunningham405@stephencunningham4053 жыл бұрын
  • Thanks for sharing 👍

    @RWATraineeElectrician@RWATraineeElectrician3 жыл бұрын
  • Excellent good explanation. Thanks

    @HH-oi8hn@HH-oi8hn3 жыл бұрын
  • As always best video on KZhead

    @user-yp9bx9tj3r@user-yp9bx9tj3r3 жыл бұрын
  • Thank you for the informative video. I had a converstation tody with a young electrician who was using the 1667 ohms for TT and 7667 ohms for TN systems for maximun Zs values.... when RCD protected... Would love your opimion on this.

    @ningis21@ningis212 жыл бұрын
  • Thank you John..gl

    @leebrown3895@leebrown38953 жыл бұрын
  • And a follow up on measuring cct impedance would be spot on :)

    @Farlig69@Farlig693 жыл бұрын
  • Thank u very much mr ward

    @jdconstruction4079@jdconstruction40793 жыл бұрын
  • Thank you JW , clear and efficient as always. Please can you explain why we consider high fault currents such as 100A or 300A when the incoming supply is cut off by the suppler fuse at 60A anyway?

    @amitthakrar2093@amitthakrar20933 жыл бұрын
  • Great video thanks

    @grantrennie@grantrennie3 жыл бұрын
  • Thanks John

    @chrissmith7259@chrissmith72593 жыл бұрын
  • Top work😀

    @meltrechsler4368@meltrechsler43683 жыл бұрын
  • Great job

    @constructionKnowledge11@constructionKnowledge113 жыл бұрын
  • Thanks John another good bit of technical/mathematical information, Question for you ,,,what figure do you apply on the electrical certificate in the maximum Zs value allowed.

    @terrybroome9229@terrybroome92293 жыл бұрын
    • Usually the 80% values.

      @jwflame@jwflame3 жыл бұрын
  • You sir are what we call.. a fucking legend. Thankyou

    @SeanyyBoy_@SeanyyBoy_6 ай бұрын
  • thanks I finally got it

    @kyr34@kyr342 жыл бұрын
  • Does the use of the manufacturers data sheet values not create a trap for young players in regards to replacing the Circuit Breaker at a later time with a different manufacturers CB potentially creating a non compliances issue? (in regards to the impossible impedance values)

    @NZHippie@NZHippie3 жыл бұрын
  • The IET refuse to add another table into the BS7671 with the 80% values attached. This table is in the GN3 and contains the values required for 99.9% of tests. The GN1 states that the values shown in BS7671 are primarily for designers, but I don’t see the point if the inspector & tester still carries out the tests with next to no load on the circuits. The BS7671 is also misleading with the calculation given in appendix 3. The Cmin value has already been factored into the tables in Part 4 and therefore only the 80% calculation is required. Ok, rant over. Good work JW.

    @spcyman7209@spcyman72093 жыл бұрын
  • If my measured zs is over the values permited for type d (20×) in bs7671, but when calculating max zs with manufacturers Ia (×17) my measured values are now under.... would the circuit still be classed as non compliant?

    @johnaphone@johnaphone3 жыл бұрын
  • Nice. Any reason the Cmin factor is 0.95?- rather than 0.94??...considering the according to ESQCR the RMS mains voltage supply can at customer terminals can be 230VAC +10%, and -6% ! Cheers

    @tomlloyd9372@tomlloyd93723 жыл бұрын
  • Thanks

    @electricalservicesmaroc@electricalservicesmaroc3 жыл бұрын
  • How did you come up with the equation? The AC supply voltage is always quoted as 230 +/- 10% which gives a min supply of 117V/160A = 1.3565 ohms which gives a much lower impedance.

    @martingregson7136@martingregson71362 жыл бұрын
  • is that chart you show maximum measured? and the book max permitted? also what is the difference and why would the book give not fully calculated values taking into account cmin and 80% factor?

    @db-bv5rs@db-bv5rs2 жыл бұрын
  • Is type D circuit breaker the only type capable of 5 second disconnection time ? as it gives a Zs value in Table 41.3 for 0.4 secs as well as 5 seconds for Type D only. Do types B and C always trip within 0.4 seconds .

    @michaelcostello6991@michaelcostello69912 жыл бұрын
  • So what do you do with the z value, measure your circuit and compare? Replace with lower resistance cables if it's exceeded?

    @mc_cpu@mc_cpu3 жыл бұрын
    • Yes, although it should just be confirming the circuit values comply. If not, then the design of the circuit is wrong.

      @jwflame@jwflame3 жыл бұрын
  • As always, another great explanation. Better than most of, if not all of my training courses.

    @barnsley1066@barnsley10663 жыл бұрын
  • Excellent video John mor calculation please

    @mohamedbutt8466@mohamedbutt84662 жыл бұрын
  • If you have a pfc of say 8Ka at a consumer unit and the mcbs are rated at 6ka , would this be a C1 on an eicr or does the main bs 88-3 fuse cover this fault current ? Struggling to find an answer thanks

    @154electrician@154electrician Жыл бұрын
    • If it's a consumer unit to BS EN 61439-3 with a maximum of 100A BS88-3 fuse supplying it, then it's rated to 16kA even if the devices in it are rated less than that. This does NOT apply for other types of installations, for those the devices must either be rated appropriately for whatever fault level exists, or have appropriate protection from upstream devices.

      @jwflame@jwflame Жыл бұрын
    • @@jwflame thank you for the reply 👍

      @154electrician@154electrician Жыл бұрын
  • How do you calculate the maximum zs for fuses since they have no curve characteristics like Mcbs? Is the maximum amps needed just the rated currently of the protective device multiplied by 1.45?

    @Skelton1996@Skelton1996 Жыл бұрын
    • Same principle, fuses do have time/current curves which are available from the manufacturer, so it's a case of finding out what the current to cause disconnection in a certain time is, and calculating the max impedance using that current and the voltage. Example data: www.lawson-fuses.com/technical-data/datasheets/

      @jwflame@jwflame Жыл бұрын
  • So what would a b4 CB be?

    @johnpurkis9872@johnpurkis98722 жыл бұрын
  • John can you do an example that shows both the ambient temperature of the installation and the max operating current of the cable, I'm sure these factors are required in the real world if you don't mind thanks.

    @angelofranklin1@angelofranklin13 жыл бұрын
    • I'd suggest the supply cable should be bigger or the breaker changed to type C

      @rossmurdoch1886@rossmurdoch18862 жыл бұрын
  • Does every electrician measure their own Z values and sign off on them. If the inspection was done by someone else they would not know the manufacturers exact tripping currents ? They might fail something that was actually ok ? Could this happen or what actually happens in practice.

    @michaelcostello6991@michaelcostello69912 жыл бұрын
  • Type B MCB 6 amps has a Zs of 7.28 ohms from Table. 230 volts/7.28 ohms = 31.6 amps when there is an earth fault. Type B Trips immediately between 3-5 times MCB 6 amps. Therefore 31.5 amps will definitely cause an instantaneous trip as it is greater than max current 5 times MCB Type B of 6 amps = 30 amps required for an instant trip. I assume that is the logic of Zs . It guarantees an instantaneous trip

    @michaelcostello6991@michaelcostello69912 жыл бұрын
  • Your a sparky God!!

    @scottbrown7049@scottbrown70493 жыл бұрын
  • Hi John

    @baase89@baase893 жыл бұрын
  • Can you do Zs calculation for MCCB and ACB pls

    @prashanthgs538@prashanthgs5386 ай бұрын
  • Not a electrician but subscribed, does not the Ohms change for length of wire?

    @robertmccully2792@robertmccully27923 жыл бұрын
    • Yes, longer length = increased resistance (ohms). There is always a maximum length that a circuit can be.

      @jwflame@jwflame3 жыл бұрын
    • @@jwflame so the Z table your showing is an average number? Sorry for my lack of not understand the math, being there is no wire length. I guess this explains it,, very minimal per thousand feet. www.bcae1.com/wire.htm#:~:text=It%27s%20resistance%20is%20approximately%201%20ohm%20per%20thousand,1%20ohm%2F1000%20ft%20or%200.001%20ohms%2Ffoot%20of%20wire.

      @robertmccully2792@robertmccully27923 жыл бұрын
    • robert mccully the cable length is dictated by Max measured Zs value and the measured Ze value of the installation. For example if the Ze was 0.3 Ohms and the circuit was protected by a type B32 CB with a maximum measured value of 1.1 Ohms, then the cable (R1+R2) would be restricted to an impedance of 0.8 Ohms. Zs=Ze+(R1+R2).

      @spcyman7209@spcyman72093 жыл бұрын
    • Hi Robert - Of course -any length of wire will have resistance - and it depends upon several things : 1, how long the wire is, 2 how thick the wire is, 3, what it is made of ( usually copper) , and its temperature. Resistance goes up with length - down with increased thickness, its "lower" with copper, "higher with" say aluminium, and goes up with temperature. Copper cable goes up in resistance by about 0.4% per degree c rise (or 0.004 times per degree C) -so if you measure a cable's resistance at say 20 degrees typical ambient - and then raise it to a typical max temp rating of 70 deg C - then that is a 50 deg C rise (70-20 deg c) - so the resistance will have gone up by 50 * 0.4% = 20% - that is: its 1.2 times its original resistance - so when we apply that 1.2 times in our circuit calculation to allow for circuits operating at higher temperatures ( which they will do especially with cables buried in thermal insulation) - we actually end up offsetting the resistance ( dividing it) by 1.2 - so what we actually are doing is multiplying by 1/1.2 = 0.8 , which is where John gets the "0.8" from The "wire itself" of course can and will be of varying length in a practical circuit . In a house for example there are several circuits feeding sockets, lights, cooker , shower - and will all have different lengths . So what we need to know is - how much overall resistance can the circuit have in order for the circuit protective device to operate correctly - and from there - we can calculate the maximum length of cable- taking into account how thick the conductors are. ( these resistances "per metre" Versus cable size are conveniently tabulated in Bs7671 - and in the electricians "guidance books) For example - in a typical house: circuits feeding sockets - this might be connected using "twin and earth" cable of 2.5mm squared conductor - whereas lights might use 1.00mm , a cooker might use 6.00mm and an electric shower 10mm ( the cable needs to be " thick enough" to carry the expected current !! - so its not just about the resistance ! ( and volt drop too ... but we wont go into that here ... ) So What we are trying to do here is find out how much resistance a circuit can have overall This "overall" circuit resistance has three essential parts - 1 - the "external" resistance ( more correctly "impedance" - given the symbol "Z") "looking back" from where the supply enters the building (and connects to the distribution board) to the "supply transformer in the street" - this part of the overall circuit is called "Ze" 2 The resistance of the circuit "line" conductor" from the distribution board to the end point of the circuit in the building - this is called "R1" 3 The resistance of the "earth conductor" - called the "circuit protective conductor" - or "CPC" from the end point of the circuit "back" to the distribution board - this is called "R2" NOW - in the event of what "we" are calling a "fault": the live conductor is assumed to be directly connected at the end of the circuit ( ie short-circuited ) to the CPC . So - you can now see that the TOTAL resistance in the circuit under this "fault condition" is the sum of resistance around the whole circuit from the supply transformer in the street - to the "short circuit" at the end of our circuit and back - which is: Ze + R1 + R2 , and we call this the "system resistance" ( or impedance ) = Zs - so - the only part "we" can "control" in our installation and calculation is the "R1 + R2" part - so when we know what "Ze" is ( usually quite low at around 0.35 ohms or so) we can calculate "Zs" by looking at the cable resistances When a fault occurs in that circuit, now we can show that the current that flows will be great enough to "blow the fuse" (ie "melt the fuse wire" ) or in more modern times such as they are now - "operate a circuit breaker" ... And ... What we are ALSO trying to achieve is to get the fuse to blow or the circuit breaker to operate in a certain time. That way - if the fuse blows quick enough - no damage is done to the circuit ( like cables heating etc) . This all comes under the idea of "Automatic Disconnection" in the case of a fault. Now it is pretty easy to see that the bigger the current - the quicker a fuse will blow ( heats up quicker) - or - in the case of a circuit breaker which relies upon a magnetic field generated in a coil within the protective device which carries the fault current to operate the cutout - the more quickly that will operate. (NOTE : there is also a Thermal device in the circuit breaker which detects lower values of fault current over varying times to operate the cutout) But - the question is - "how quick" - and this is where the "type of external supply " needs to be considered - but for a typical circuit say in a house being fed from a common type of supply where the "return earth fault path" is provided by the supply authority - called a "TN" supply - then - the disconnection time is 0.4 secs ( the table that John was referring to in BS7671)

      @eric4709@eric47093 жыл бұрын
    • Eric Churchyard that’s a very in depth explanation. So basically z is potentially friction with a safety factor. But called resistance to simplify.

      @robertmccully2792@robertmccully27923 жыл бұрын
  • ...you can use all these charts or actually use your loaf. I guess if you have 50 years' experience, then the latter. Good work, John

    @kirkthrust6116@kirkthrust611611 ай бұрын
  • Mathematicians would always use operator (arithmetic) calculations (multiplications) with largest decimals. Rounding too early just adds to errors if carrying out these arithmetic operations. Indeed the laws of arithmetic would break down at least in terms of continuous equivalence.

    @mathman0101@mathman01013 жыл бұрын
  • One dislike comes from a person who has installed the type D circuit breaker with no consideration for this 20x current requirement thing...

    @lynx911able@lynx911able3 жыл бұрын
    • lynx911able like or dislike doesnt matter. Both are good for the channel. Another think that when people dislike the vid they dont explain why

      @tonyp2878@tonyp28783 жыл бұрын
  • Does this rule apply to 3 phase

    @paulgerrard2529@paulgerrard2529 Жыл бұрын
    • Yes, the same principles apply.

      @jwflame@jwflame Жыл бұрын
  • Doing ohms law, VIR with minimum 0.95 correction factor

    @lukasbarnes@lukasbarnes2 жыл бұрын
  • Watched ze and zs destroy people's minds in college then shown on a board it's basic stuff

    @ianhill20101@ianhill201013 жыл бұрын
    • Looool

      @827181@8271813 жыл бұрын
  • Please share the name of the book??

    @ramashisbanerjee8342@ramashisbanerjee8342 Жыл бұрын
    • shop.theiet.org/requirements-for-electrical-installations-iet-wiring-regulations-eighteenth-edition-bs-7671-2018-a2-2022

      @jwflame@jwflame Жыл бұрын
  • OMG. My girl just came back tipsy drunk with her BFF's and they are all randy as feck after this CV19 shutdown stuff and are all begging me for a good service. I had to refuse them all because JW has a new video.

    @Drew-Dastardly@Drew-Dastardly3 жыл бұрын
    • Send her around to me. I can do an oil and filter change at a very reasonable price.

      @stupot_64@stupot_643 жыл бұрын
    • @@stupot_64 It's OK Stuart I got it all in hand, slippery lube and all... but they have to wait for me to finish my JW video.

      @Drew-Dastardly@Drew-Dastardly3 жыл бұрын
    • @@Drew-Dastardly Just make sure you change the filter. The masks don't last forever.

      @stupot_64@stupot_643 жыл бұрын
    • Is this comment full of slangs or car is broken ?

      @zanimljivastruja7511@zanimljivastruja75113 жыл бұрын
    • 🙄

      @grantrennie@grantrennie3 жыл бұрын
  • If you were to use the actual value for a specific model of class C circuit breaker, for example, what's the ongoing responsibility in the future if that circuit breaker were to fail and be replaced by some "equivalent" class C breaker that trips at a higher current? I would have expected the relevant authorities to require installations to allow for the worst case for a particular class of breaker, not the typical performance of a specific brand/model.

    @PaulSteMarie@PaulSteMarie3 жыл бұрын
    • Responsibility is with the person replacing the circuit breaker - it's up to them to test the circuit to ensure the item they are installing is suitable. Mixing different manufacturers devices in the same enclosure isn't generally permitted either.

      @jwflame@jwflame3 жыл бұрын
    • Whoever changes the circuit breaker should be testing the circuit anyway. Then they will know if the loop impedance is satisfactory for the new device that they fit. If they do not bother testing the circuit, they are not completing their task properly.

      @brewertonpaul@brewertonpaul3 жыл бұрын
  • why not use minimum tripping current= In x 3 for type B since its between 3x-5x. Why use 5x

    @acikgozerkay@acikgozerkay3 жыл бұрын
    • Because the tripping characteristics of mcbs have a tolerance you must always calculate based on maximum current values for safety. Its no good working on the assumption that only 30A will flow through a circuit protected by a B10 if in fact 50A is the actual value.

      @cbcdesign001@cbcdesign0013 жыл бұрын
  • If a circuit is protected by an RCB then why does the loop impedance need to be low ..surely a phase to PE fault would trip the RCB

    @ol-np8sy@ol-np8sy2 жыл бұрын
    • RCDs do not work on phase-neutral faults, and on TN supplies if phase-earth is too high, it's usually the case that phase-N is also too high. Using RCDs as fault protection for phase-earth faults is only appropriate when there is no other option such as a TT supply.

      @jwflame@jwflame2 жыл бұрын
  • What happens when a 61009 fails the maximum Zs but passes the 5x test?

    @stevenbrooks8323@stevenbrooks83233 жыл бұрын
    • Acceptable for a TT system where the use of RCDs for fault protection is inevitable due to the high Ze. Not acceptable on a TN system where RCDs are used as additional protection.

      @jwflame@jwflame3 жыл бұрын
  • Wouldn’t you be multiplying 1.4375 by 80%? Rather than the 95% value?

    @f1reguy587@f1reguy5872 жыл бұрын
    • 80% is used to obtain 'real world' values which allow for temperature differences in the conductor. If that is applied, it's done at the end. It's an approximation and is used to avoid having to calculate the difference for conductor temperature for each individual circuit. 0.95 is a correction factor for supply voltage differences, and is always included.

      @jwflame@jwflame2 жыл бұрын
  • 80% ... Resistance increases with temperature rise.

    @gbgb8878@gbgb8878 Жыл бұрын
  • you forgot Type A from Siemens . Type A =2x-3x @ 0.57 sec you can see diagram from A tripping Characteristic

    @ASEAngelica@ASEAngelica2 жыл бұрын
  • I thought type D was only 10x it’s rating not 20x???

    @jamesmiller8610@jamesmiller86102 жыл бұрын
    • Depends on the manufacturer - the generic specification is between 10x and 20x, so 20x to guarantee tripping, but it's better to use the specifications for the actual device being used, as some will be lower than 20x.

      @jwflame@jwflame2 жыл бұрын
    • Thanks John much appreciated.

      @jamesmiller8610@jamesmiller86102 жыл бұрын
  • hi

    @MrTChrisso@MrTChrisso Жыл бұрын
  • Or you could skip two multiplications by assuming the voltage is 174.8 V.

    @bdf2718@bdf27183 жыл бұрын
  • But, there is no way the resistance of a circuit breaker would ever be that high. If I had a circuit breaker with a 1 ohm impedance, and had 30 Amps going though it, that would be 900 Watts. Typical impedance of a breaker is milliohms

    @MultiMeterChannel@MultiMeterChannel3 жыл бұрын
    • Maximum impedance applies to the circuit as a whole, not just the protective device.

      @jwflame@jwflame3 жыл бұрын
  • why don't give your followers to download this table or handy relatives information for your videoe you talking so fast with up and down voice which difficult to follow from nonnative English

    @alimanaal-atefi3622@alimanaal-atefi3622 Жыл бұрын
  • Just divid by the lowest voltage, stop making work

    @MrPowellfactor@MrPowellfactor Жыл бұрын
  • I use the same formula for years already And you can calculate the 60947-2 MCCBs for Schneider and ABB. ABB @100% Zs: 230VxCmin / I3 [A] x 1.2 Schneider @100% Zs: 230VxCmin / Im [A] x 1.1 I3 and Im is the magnetic or instant release current.

    @plaveczm@plaveczm3 жыл бұрын